    I am running electric to my new 5hp, 60 gallon air compressor. I read a supplement to the directions and they said to double the amps on the curcuit breaker to the maximum that is on the motor which is 22.5 amps. That would be 50 amps. The motor has #10 wire going to it which is good for 30 amps. I was planning on putting it on a 30 amp breaker but was just wondering why the directions said to double the amps and was also wondering what amp breaker everyone else was running to their compressors of similar size.
     
  2. Grabber5.0

    Grabber5.0 Gear-head wannabe

    Joined:
    Mar 9, 2002
    Messages:
    2,199
    Likes Received:
    3
    Trophy Points:
    127
    Location:
    Kansas City, MO
    Vehicle:
    71 Grabber
    Pretty sure mine is a 30 amp breaker, I used my 220 line I set up for nutt's plasma cutter, and put a plug on some 12ga wire hooked up to the compressor.
     
  3. Dan Starnes

    Dan Starnes Original owner

    Joined:
    Mar 10, 2002
    Messages:
    5,235
    Likes Received:
    51
    Trophy Points:
    146
    Location:
    West Central IL
    Vehicle:
    Stallion, 72 Grabber, Sprint, 77 4dr Maverick
    I have a 6hp,, have never heard it stated like that before. I am running 12 gauge wire and a 30 amp breaker..had it for 10 years, 2 different houses. Never ever tripped the circuit.
     
  4. Cleaver

    Cleaver Member

    Joined:
    Dec 31, 2003
    Messages:
    572
    Likes Received:
    3
    Trophy Points:
    97
    Location:
    MD
    Vehicle:
    Chel
    Nearly the same here. 6 HP, 80 gallon, 12 ga wire, 30 amp breaker.

    Cleaver
     
  5. Ronald Hopkins

    Ronald Hopkins Member

    Joined:
    Mar 22, 2002
    Messages:
    723
    Likes Received:
    64
    Trophy Points:
    116
    Location:
    Morristown Tennessee
    Vehicle:
    1972 Comet GT
    I have my compressor that is a 6 hp. 60gallon tank wired up to 220 volt double pole 30 amp breakers.
     
  6. Mavaholic

    Mavaholic Growing older but not up!

    Joined:
    Mar 9, 2002
    Messages:
    14,984
    Likes Received:
    190
    Trophy Points:
    258
    Location:
    Live Oak, FL
    Vehicle:
    Original 72 Sprint Owner, 71 Comet GT, 57 Ranchwagon, 57 4 dr Wagon
    Most Harry home owner shop compressors have a 6 hp which is rated around 15 amps so having a 30 amp breaker is doubling the rated value. I know you bought a 2 stage so your current rating is going to be higher because it probably has a bigger motor. The reason for doubling the circuit breaker is because current is highest at start up. It can be 10 times the motors rated amps. But it only last for a secong and the circuit breaker wont react that fast. Therefore you should put at least a 40 amp breaker on it. During normal operation it will probably draw less than 20 amps.
     
  7. maverick1970

    maverick1970 MCG State Rep

    Joined:
    Sep 9, 2003
    Messages:
    7,372
    Likes Received:
    58
    Trophy Points:
    242
    Location:
    Missouri
    Vehicle:
    69 1/2, 70 Maverick and 71 Grabber
    Most motors will be labled with current and start-up current figures. If undersized you will most likely see the breaker tripping when starting up under pressure.
     
  8. NICK DOMINICK

    NICK DOMINICK MCCI Virginia State rep.

    Joined:
    Oct 24, 2003
    Messages:
    1,521
    Likes Received:
    84
    Trophy Points:
    160
    Garage:
    1
    Location:
    Burke, Virginia
    Vehicle:
    1972 Grabber 302, 1973 Maverick my first car that is under restoration, 1972 Grabber and 1976 Maverick parts cars, 2012 Mustang GT, 2001 Lightning
    I have my compressor on a 30 amp breaker and have had no problems so far. I ran #8 wire so I can up the amps if need be but I don't think I will. Everything turned out great!!
     